RSC Device Interface Services
The RSC Device Interface Services provide a range of functions for accessing properties of the operating system and the controller hardware. You can call the information with the following interfaces and defined parameters. The following headers are required to use the service; integrate these headers via #include, if necessary:
  • Arp\Device\Interface\Services\IDeviceControlService.hpp
  • Arp\Device\Interface\Services\IDeviceInfoService.hpp
  • Arp\Device\Interface\Services\IDeviceSettingsService.hpp
  • Arp\Device\Interface\Services\IDeviceStatusService.hpp
  • Execution of RSC services can take some time. For this reason, avoid direct calls from ESM tasks.
  • Exceptions thrown by RSC service calls should always be explicitly caught and handled by RSC clients.
  • In addition, the underlying type of each RscVariant returned by RSC service calls should never be assumed but should always be checked before performing any other operation on that object.
TheIDeviceControlService RSC interface provides the following methods to control the device:
  • void RestartDevice ();
    This method reboots the PLC.
    Note: T must not be invoked within an ESM task.
  • AccessErrorCode ResetToFactoryDefaults (Uint16 resetType);
    With resetType == 1 :
    All user-specific data is deleted (settings, programs, users, etc.). The current PLCnext Technology firmware remains unchanged.
    With resetType == 2 :
    In addition to deleting the user-specific data, the firmware of the controller is reset to the default state.
  • AccessErrorCode StartFirmwareUpdate (Uint16 updateType);
    This function starts to update the firmware using a previously downloaded firmware container. The updateType parameter has to be set to 0. Other values are reserved for future extensions.
IDeviceInfoService
The IDeviceInfoService RSC interface enables read access to device information with the following methods:
  • RscVariant<512> GetItem(const RscString<512>& identifier)
    The GetItem() method reads the status value of a parameter.
  • void GetItems(GetItemsIdentifiersDelegate identifiersDelegate,
                  GetItemsResultDelegate resultDelegate)
    The GetItems() method reads the status values of several parameters.
The following parameters are available in the IDeviceInfoService RSC interface for calling of information:
Parameter Data type Description
General.DeviceClass UInt32 The DeviceClass parameter specifies the device class. At the moment, only ProgrammableLogicController is supported.
0: Undefined
1: ProgrammableLogicController
2: BusCoupler
3: Switch
General.VendorName String The VendorName parameter indicates the name of the manufacturer.
General.ArticleName String The ArticleName parameter indicates the device name.
General.ArticleNumber String The ArticleNumber parameter indicates the order number of the device.
General.SerialNumber String The SerialNumber parameter indicates the serial number of the device.
General.CloudUuid String The CloudUuid parameter indicates the Proficloud UUID of the device
General.Firmware.Version String The FirmwareVersion parameter indicates the firmware version of the device. Here, the 5-level notation (Major, Minor, Patch, Build, Status) is used.
General.Firmware.VersionMajor Byte The firmware version year is indicated without the first two digits. E.g., “2019” is indicated as 19.
General.Firmware.VersionMinor Byte FirmwareVersionMinor
General.Firmware.VersionPatch Byte FirmwareVersionPatch
General.Firmware.VersionBuild UInt32 FirmwareVersionBuild
General.Firmware.VersionStatus String FirmwareVersionStatus
General.Firmware.BuildDate String FirmwareBuildDate
ISO 8601 format <YYYY>-<MM>-<DD>
General.Firmware.BuildTime String FirmwareBuildTime
ISO 8601 format <hh>:<mm>:<ss>
General.Hardware.Version String The HardwareVersion parameter indicates the hardware version of the device.
General.Fpga.Version String The FPGAVersion parameter indicates the FPGA version of the device. Here, the 3-level notation (Major, Minor, Patch) is used.
General.Fpga.VersionMajor Byte FPGAVersionMajor
General.Fpga.VersionMinor Byte FPGAVersionMinor
General.Fpga.VersionPatch Byte FPGAVersionPatch
General.UniqueHardwareId String Sha256 Hash (32byte) hexadecimal coded as string
General.SPNS.Fpga.Version String FPGA version of the SPNS (only for devices with integrated safety controller)
General.SPNS.Fpga.VersionMajor Byte SPNS FPGA version, major
General.SPNS.Fpga.VersionMinor Byte SPNS FPGA version, minor
General.SPNS.Fpga.BuildVersion Unsigned32 SPNS FPGA build version
General.SPNS.Firmware.Version String SPNS firmware version
General.SPNS.Firmware.VersionMajor Byte SPNS firmware version, major
General.SPNS.Firmware.VersionMinor Byte SPNS firmware version, minor
General.SPNS.Firmware.BuildVersion Unsigned32 SPNS firmware build version
Interfaces.Ethernet.Count Byte The NoOfNetworkInterfaces parameter indicates the number of network interfaces.
Interfaces.Ethernet.{adapterIndex}.{port}.Mac String
The Mac parameter indicates the MAC address of the selected network interface.
adapterIndex: 1, 2,...
port = 0 for the interfaceMAC
port = 1, 2,... for the portMAC
MAC data format is alwaysAA:BB:CC:DD:EE:FF .
Cpu.Cores.Count Byte
From firmware version 2023.0 LTS:
The parameter NumberCpuCores provides the count of the CPU cores of the controller.
With the IDeviceSettingsService, several settings of the device can be read or written.
Therefore, this service provides four methods (linked to the related description in the 2022.0 LTS API documentation):
These possible settings are supported:
Parameter
Data type
Description
General.Function
String
Function description appropriate to the PROFINET specification. The parameter is retained in the I&M2 data and still available after a firmware update. (Projects/Default/Device/Interface/Di.User.config).
Valid characters: 0x20 .. 0x7e
Max. string length: 32 characters.
General.Location
String
Installation location of a device appropriate to the PROFINET specification. The parameter is retained in the I&M2 data and still available after a firmware update. (Projects/Default/Device/Interface/Di.User.config)
Interfaces.Ethernet.{AdapterIndex}.IpAssign
Byte
AdapterIndex: 1, 2, ...
IpAssign is the configuration type of the network adapter’s IP Address.  Values are:
  • 0: Static
  • 2: DHCP
Default: 0
Note: DHCP only works on adapters without PROFINET function (for settings, see the respective hardware documentation).
The value becomes active after a restart of the device. If the value is Static then the values of Ip and Subnet are taken.
Error values:
  • UnknownSetting: The AdapterIndex parameter is not supported.
  • InvalidParameter: Value is illegal.
  • IncompatibleType: Parameter is not of type Byte.
String
Ip is the IP Address of a network adapter. Format: aaa.bbb.ccc.ddd where each value must contain decimal numbers between 0..255
The value is stored permanently. When the value is read then the last written value is returned.
Error values:
  • IncompatibleType: Value is not a String.
  • InvalidFormat: Value does not correspond to the defined format.
  • OutOfRange: At least one value is larger than 255.
Interfaces.Ethernet.{AdapterIndex}.Subnet
String
AdapterIndex = 1, 2, ...
Subnet is the subnet of a network adapter. Format: aaa.bbb.ccc.ddd where each value must contain decimal numbers between 0..255
Error values:
Interfaces.Ethernet.{AdapterIndex}.DefaultGateway
String
DefaultGateway is the default gateway of a network adapter. Format: aaa.bbb.ccc.ddd where each value must contain decimal numbers between 0..255
Error values:
Interfaces.Ethernet.{AdapterIndex}.DnsNameservers
String
The DnsNameservers parameter contains a list of one or up to three DNS server names. If the list contains more than one name then they must be separated by a space character.
Format:
aaa.bbb.ccc.ddd[ eee.fff.ggg.hhh.iii][jjj.kkk.lll.mmm]
Default value: 8.8.8.8 8.8.4.4
Error values:
Ntp.NtpServers
String
List of all NTP servers. The server can be defined as IP address or in DNS format. The list should always contain the list of all NTP servers, otherwise the list on the device is incomplete.
If the parameter contains an empty string, then all servers are deleted except the fallback server.
Format:serverID[ serverID]...
Example:127.127.1.0 ntp.server1.com
Max. string length: 253 characters.
Note: By writing NTP Server configuration with this service, dedicated NTP settings like min./max. polling times that have been configured via the Date and Time WBM page are removed.
Rtc.DateTime
String
Date and time of the controller
ISO 8601 format: <YYYY>-<MM>-<DD>T<hh>:<mm>:<ss>+-<hh>:<mm>
Note: Currently, a given time zone is ignored when writing this string. When reading, +00:00 is responded.
Rtc.Time
String
Time of the controller
ISO 8601 format: <hh>:<mm>:<ss>
Rtc.Date
String
Date of the controller
RemovableStorage.1.State
String
Status of an external SD card.
Note: Setting a status is only possible with admin user role. You can also make the setting via the WBM page SD Card
Supported values for writing, done with a WriteValue() or WriteValues() function:
  • request_deactivation
  • request_activation
A restart is required to finalize the procedure.
Read can return following status:
  • activated: The external SD card is activated.
  • deactivated: The external SD card is deactivated.
  • request_deactivation: The deactivation is requested, a restart is required.
  • request_activation: The activation is requested, a restart is required.
  • not_supported: The setting is not supported on this device.
General.Watchdog.Plc.Restart
Byte
Definition of the behavior of the Plc component of the PLCnext Technology runtime after a system watchdog occurred.
0: The Plc component of the PLCnext Technology runtime will not restart
1: The Plc component of the PLCnext Technology runtime restart automatically
Default is 0.
Error codes
The values of AccessErrorCode and their meanings are:
Value Code
None 0
UnknownError 1
UnknownSetting 2
AuthorizationFailure 3
IncompatibleType 4
InvalidFormat 5
InvalidParameter 6
OutOfRange 7
Naming of LAN interfaces and LAN ports on controllers
The following table provides an overview to the different PLCnext Control devices and the naming of their LAN interfaces and ports. The naming of a port is the same as printed on the housing, e.g. X1.
PLCnext Control Naming on the housing Interface no. in IDeviceSettingsService
AXC F 2152
AXC F 1152
Internal interfaces:
  • TCP/IP (LAN 1)
    • Port X1
    • Port X2
  • TCP/IP (LAN 1)
    • Interface no. = 1
External interfaces via left-aligning (AXC F 2152 only):
  • TCP/IP (EXT LAN 1)
    • Port X1
External interfaces via left-aligning:
  • TCP/IP (EXT LAN 1) - switched mode
    • Interface no. = 2
AXC F 3152 Internal interfaces:
  • TCP/IP (LAN 1)
    • Port X1
  • TCP/IP (LAN 2)
    • Port X2
  • TCP/IP (LAN 3)
    • Port X3
  • TCP/IP (LAN 1)
    • Interface no. = 1
  • TCP/IP (LAN 2)
    • Interface no. = 2
  • TCP/IP (LAN 3)
    • Interface no. = 3
    • Port X1
    • Interface no. = 4
RFC 4072s Internal interfaces:
  • TCP/IP (LAN 1)
    • Port LAN 1
  • TCP/IP (LAN 2)
    • Port LAN 2
  • TCP/IP (LAN 3) - Switched Mode
    • Port LAN 3.1
    • Port LAN 3.2
  • TCP/IP (LAN 1)
    • Interface no. = 1
  • TCP/IP (LAN 2)
    • Interface no. = 2
    • Interface no. = 3
The IDeviceStatusService RSC interface enables read access to status information.
  • The status value of a parameter is read with the GetItem() method.
  • The status values of several parameters are read with the GetItems() method. Use the deviceStatusService.GetItem("Parameters") method to call status information.
The following parameters are available for calling information:
Status.Cpu.{Core}.Load.Percent
Byte
The CPU.{Core}.Load status indicates the processor load of the selected processor core of the device as a percentage. Cores are identified by numbers 1 and higher while Core 0 indicates the entire processor load.
Core:  0, 1, 2, ...
Value range:
0% ... 100% where 100% would be reported as 0x64
Status.Memory.Usage.Percent
Byte
The Memory.Usage status indicates the memory usage of the device as a percentage. With this parameter, the percentage depends only on free memory; reclaimable memory is not included in the calculation.
Value range:
Status.Memory.Usage.Percent.Actual
(available from firmware 2023.0 LTS)
UInt8
The Memory.Usage status indicates the memory usage of the device as a percentage, as above. But with this parameter, the percentage depends on available memory which includes free and reclaimable memory.
Value range:
0% ... 100%
Status.ProgramMemoryIEC.Usage.Percent
Byte
The ProgramMemoryIEC.Usage status indicates the program memory usage of the IEC runtime of the device as a percentage.
Value range:
Status.DataMemoryIEC.Usage.Percent
Byte
The DataMemoryIEC.Usage status indicates the data memory usage of the IEC runtime of the device as a percentage.
Value range:
Status.RetainMemory.Usage.Percent
Byte
The RetainMemory.Usage status indicates the retain memory usage of the device as a percentage.
Value range:
Status.Board.Temperature.Centigrade
Int8
The Board.Temperature status indicates the temperature of the interior of the device in °C.
Status.Board.Humidity
Byte
The Board.Humidity status indicates the relative humidity in the device.
Value range:
Note concerning AXC F 3152: This feature is only available up to hardware revision 03.
Status.Cpu.Temperature.Centigrade
Int8
For RFC 4072S only:
The CPU.Temperature status indicates the temperature of the processor in °C.
Status.Overlay.BootDevice
String
The Overlay.BootDevice status indicates the mounting of the overlay file system.
Values:
  • internalSD
  • externalSD
Status.RemovableStorage.1.Present
Bool
The RemovableStorage.1.Present status indicates whether an external SD card  is present.
Values:
  • true: SD card present
  • false: No SD card present
Status.RemovableStorage.1.State
String
TheRemovableStorage.1.State status indicates the state of the external SD card.
Values:
Status.Fan.Supported
Bool
TheFan.Supported status indicates whether the PLCnext Control device supports a fan.
Values:
  • true: Fan is supported.
  • false: Fan is not supported.
For most controllers a fan is optional. Only ifFan.Supported is true the other Fan status indicators are supported (see next rows in this table).
Status.Fan.Plugged
Bool
TheFan.Plugged status indicates whether a fan is plugged.
Values:
  • true: A fan is plugged.
  • false: No fan is plugged.
Status.Fan.Defect
Bool
TheFan.Defect status indicates whether the fan is defect.
Values:
  • true: The fan is defect.
  • false: The fan is OK.
Status.Fan.Maintenance Bool
TheFan.Maintenance status indicates whether the fan needs to be maintained.
Values:
  • true: The fan needs maintenance.
  • false: No maintenance required.
Status.Fan.Speed.Level
UInt8
TheFan.Speed.Level status indicates the speed of the fan.
Values:
  • 128: Off
  • 231: Low
  • 242: Medium
  • 255: High
Status.Fan.Timestamp
String
TheFan.Timestamp status indicates date and time when the fan was calibrated the last time.
Format:DD.MM.YYYY hh:mm
Status.RamDisk.{RamDiskIndex}.Usage.Percent
Byte
For RFC 4072S only:
TheRamDisk.{RamDiskIndex}.Usage.Percent status indicates the memory usage of the RAM disc(s) as a percentage.
Value range:
0% ... 100% where 100% would be reported as0x64
RamDiskIndex = 1, 2, ... indicating the index of the RAM disc; currently, only one RAM disc is supported, so that the index is always1.
UInt32
For RFC 4072S only:
TheRamDisk.{RamDiskIndex}.Usage status indicates the absolute memory usage of the RAM disc(s).
Status.Ups.ChargeLevel
Int32
From firmware release 2022.6 for PLCnext Control devices with an integrated UPS:
The Ups.ChargeLevel status indicates the current charge status of the UPS in % (relative state of charge).
Status.Ups.Health
Int32
The Ups.Health status indicates the content of the safety status register of the UPS controller. The bits HWARN and HFAIL contained in the safety status register are evaluated and the result is provided as Int32 value.
Values:
  • OK: 0
  • HWARN: 1
  • HFAIL: 2
Status.Ups.Diagnostics
String
The Ups.Diagnostics status indicates the current charge status of the UPS in % and the content of the UPS controller's safety status register. The bits contained in the safety status register are evaluated in the same way as with the service Status.Ups.Health (see row above).
The return values are provided in a string, divided by a blank.
Examples:
  • UPS charge status is 75 % and HWARN is set:
    75 1
  • UPS charge status is 75 % and HFAIL is set:
    75 2
Status.RunStopSwitch.Position
String
The status service Status.RunStopSwitch.Position can be used to query the switch position of the mode selector switch (Run/Stop/MReset).
This service is only available if the device supports a mode selector switch. This can be queried with the status service Status.RunStopSwitch.Supported.
Return values:
  • Unknown = Default value / Unknown state
  • Run = Mode selector switch in position Run
  • Stop = Mode selector switch in position Stop
  • MReset = Mode selector switch in position MReset
Bool
The status service Status.RunStopSwitch.Supported can be used to query whether a device has a mode selector switch.
Return values:
  • false = Mode selector switch is not supported
  • true = Mode selector switch is supported
Status.PowerSupply.X1 and
Status.PowerSupply.X2
Bool
From firmware version 2023.0 LTS for RFC 4072R only:
The RFC 4072R as a dedicated redundancy controller is equipped with redundant power supplies.
The status services Status.PowerSupply.X1 and Status.PowerSupply.X2 can be used to query whether a device is supplied with power at the X1 and the X2 connector.
Return values for each X1 and X2:
  • false = Voltage is not supplied at that connector
  • true = Voltage is supplied at that connector
You can also call status information about the LED states via the IDeviceStatusService interface.
The colors of the LEDs are represented as follows, normally in the high word (HW) of the return value:
public enum LedColor : ushort
   Green = 1,
   Yellow = 2,
   Red = 4
The status of the LEDs is represented as follows, normally in the low word (LW) of the return value:
public enum LedStates : ushort
   Off = 0,
   On = 1,
   Flashing_0_5_Hz = 2,
   Flashing_2_Hz = 3,
   Alternating_0_5_Hz = 4,
   Alternating_2_Hz = 5
IEC runtime system LEDs
Status.Leds.Runtime.Run UInt32 Runtime RUN LED (HW: color, LW: status)
Status.Leds.Runtime.Fail UInt32 Runtime FAIL LED (HW: color, LW: status)
Status.Leds.Runtime.Debug UInt32 Runtime DEBUG LED (HW: color, LW: status)
Axioline LEDs
Status.Leds.Axio.D UInt32 AXIO master D LED (HW: color, LW: status)
Status.Leds.Axio.E UInt32 AXIO master E LED (HW: color, LW: status)
PROFINET LEDs
Status.Leds.Pnio.Bf_C UInt32 Pnio controller BF LED (HW= color, LW= status)
Status.Leds.Pnio.Bf_D UInt32 Pnio device BF LED (HW= color, LW= status)
Status.Leds.Pnio.Sf UInt32 Pnio controller SF LED (HW= color, LW= status)
Calling network status information via IDeviceStatusService
You can also call status information about the network states via the IDeviceStatusService interface:
Status.Interfaces.Ethernet.{adapterIndex}.{port}.Baudrate
Byte
adapterIndex = 1, 2, ...
port = 1, 2, ...
The Baudrate status indicates the current speed of the interface:
1: 10 Mbps
2: 100 Mbps
3: 1000 Mbps
Status.Interfaces.Ethernet.{adapterIndex}.{port}.Duplex
Byte
adapterIndex: 1, 2, ...
port: 1, 2, ...
The Duplex status indicates the current duplex mode of the interface:
1: half duplex
2: full duplex
Status.Interfaces.Ethernet.{adapterIndex}.{port}.Link
Byte
port: 1, 2, ...
The Link status indicates the link status of the interface:
0: linkDown
1: linkUp
String
Ip is the address of the network adapter.
Format:
Note: While the IDeviceSettingsService reads the IP settings from the Interfaces file,
the IDeviceStatusService reads the current values from the interface!
Error values:
String
Subnet is the subnet mask of a network adapter.
Format:
aaa.bbb.ccc.ddd where each value must contain decimal numbers between 0..255.
Error values:
String
Format:
Error values: