Notifications registered by the PLCnext Runtime System
The following tables show the notifications that are predefined in the PLCnext Runtime System and will be issued by the PLCnext Runtime System.
Note: For security-related notifications, see Security notifications of PLCnext Runtime.
Compatibility
The SenderName declarations have changed over time. With firmware 2020.6 they have been consolidated and will now stay this way.
Due to breaking changes in the structure of notification archives with firmware 2022.0 LTS, downgrading to a former firmware release causes an exception. After resetting the device to Default setting Type 1 (see Factory Reset),  existing notification archives will be closed and renamed. Then, an archive with appropriate structure for the firmware is generated, with a first notification in it which points to the renamed archive from firmware 2022.0 LTS.
Severity levels
In the Notifications WBM page, these icons are displayed for the different severity levels:
  • icon for internal severity Internal
  • icon for information severity Information
  • icon for warning severity Warning
  • icon for error severity Error
  • icon for critical severity Critical
  • icon for fatal error severity Fatal
Note: As of firmware version 2023.6, notifications with the severity Internal are no longer logged.
Notifications by SenderName
The notifications in the following sections are grouped by their SenderName and ordered by their NotificationName. Newest entries are marked green in the Availability column.
Note: All notifications listed below are sent with Registered state, except for the System Manager's Arp.System.Acf.SystemManager.Startup notification which is sent with an Unregistered state.
Alarms
These Notifications are only shown here, because they are used internally by the implementation. These notifications are not intended to be used or sent directly. Instead, the designated methods of the AlarmServer should be used. It is recommended to read the Alarms description before working with these notifications.
From firmware version 2023.6 alarm notifications (Arp.Services.Alarms.Log.*) are logged into a separate archive alarms (file: /opt/plcnext/projects/Default/Services/NotificationLogger/alarms.config).
Note: If the notification is generated by the embedded OPC UA® Server then the NotificationName ends with .eUAServer. If generated by a function block then the NotificationName ends with .eCLR.
NotificationName ↓ Severity PayloadTypeName Availability
Arp.Services.Alarms.Log.AcknowledgeRequest.eUAServer or
Arp.Services.Alarms.Log.AcknowledgeRequest.eCLR
Internal Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.Services.Alarms.Log.AcknowledgeRequest2.eUAServer or
Arp.Services.Alarms.Log.AcknowledgeRequest2.eCLR
Internal Arp::System::NmPayload::Alarms::Internal::AckConfPayload from 2020.6
Arp.Services.Alarms.Log.AddAlarm.eUAServer or
Arp.Services.Alarms.Log.AddAlarm.eCLR
Internal Arp::System::NmPayload::Alarms::Internal::AlarmPayload from 2019.0 LTS
Arp.Services.Alarms.Log.AddComment.eUAServer or
Arp.Services.Alarms.Log.AddComment.eCLR
Arp.Services.Alarms.Log.ConfirmRequest.eUAServer or
Arp.Services.Alarms.Log.ConfirmRequest.eCLR
Arp.Services.Alarms.Log.ConfirmRequest2.eUAServer or
Arp.Services.Alarms.Log.ConfirmRequest2.eCLR
Arp.Services.Alarms.Log.NewState.eUAServer or
Arp.Services.Alarms.Log.NewState.eCLR
AlarmServer
Configurable alarms depending on the alarm server are available from firmware 2024.0 LTS.
Arp.Services.AlarmServer.Error Error Arp::System::Nm::StringPayload from 2024.0 LTS
Arp.Services.AlarmServer.Info Info Arp::System::Nm::StringPayload from 2024.0 LTS
Arp.Services.AlarmServer.Warning Warning Arp::System::Nm::StringPayload from 2024.0 LTS
Axioline
Arp.Io.Axioline.Configuration.Error Error Arp::System::NmPayload::Io::Axioline::AxioServiceErrorPayload from 2023.0 LTS
Arp.Io.Axioline.Device.Error Error Arp::System::NmPayload::Io::Axioline::AxioDeviceDiagPayload from 2023.0 LTS
Arp.Io.Axioline.Device.Info Info Arp::System::NmPayload::Io::Axioline::AxioDeviceDiagPayload from 2023.0 LTS
Arp.Io.Axioline.Device.Warning Warning Arp::System::NmPayload::Io::Axioline::AxioDeviceDiagPayload from 2023.0 LTS
Arp.Io.Axioline.Error Error Arp::System::NmPayload::Io::Axioline::AxioStatePayload from 2020.0 LTS
Arp.Io.Axioline.Parameterization.Error Error Arp::System::NmPayload::Io::Axioline::AxioPdiErrorPayload from 2023.0 LTS
Arp.Io.Axioline.StateChanged Info Arp::System::NmPayload::Io::Axioline::AxioStatePayload from 2020.0 LTS
Arp.Io.Axioline.Warning Warning Arp::System::NmPayload::Io::Axioline::AxioStatePayload from 2020.0 LTS
DataLogger
Arp.Services.DataLogger.Error Error Arp::System::Nm::StringPayload from 2020.3
Arp.Services.DataLogger.Info Info Arp::System::Nm::StringPayload from 2020.3
Arp.Services.DataLogger.Session.RemovedOnException Error Arp::System::NmPayload::Services::DataLogger::ExceptionInformationPayload from 2024.0 LTS
Arp.Services.DataLogger.StatusChanged Info Arp::System::Nm::StringPayload from 2020.3
Arp.Services.DataLogger.Warning Warning Arp::System::Nm::StringPayload from 2021.6
Device Interface
Arp.Device.Interface.EthernetLinkStateChanged Info Arp::System::NmPayload::Device::EthernetLinkStatePayload from 2019.0 LTS
Arp.Device.Interface.ExtensionModulesState Info Arp::System::NmPayload::Device::PciDeviceStatePayload from 2019.0 LTS
Arp.Device.Interface.FanControl.CalibrationStarted Info Arp::System::Nm::StringPayload from 2020.6
Arp.Device.Interface.NetworkConfigurationChanged Info Arp::System::NmPayload::Device::NetworkConfigurationChangedPayload from 2019.0 LTS
Arp.Device.Interface.NetworkConfigurationFailed Error Arp::System::NmPayload::Device::NetworkConfigurationChangedPayload from 2019.0 LTS
Arp.Device.Interface.NtpConfigurationChanged Info Arp::System::NmPayload::Device::NtpConfigurationChangedPayload from 2020.3
Arp.Device.Interface.NtpConfigurationFailed Error Arp::System::NmPayload::Device::NtpConfigurationChangedPayload from 2020.3
Arp.Device.Interface.PowerSupplyStatus.Changed Info Arp::System::NmPayload::Device::PowerSupplyStatusPayload from 2023.0 LTS
Arp.Device.Interface.PowerSupplyStatus.Warning Warning Arp::System::NmPayload::Device::PowerSupplyStatusPayload from 2023.0 LTS
Arp.Device.Interface.RealTimeClock.BatteryCapacityFailure Warning Arp::System::Nm::StringPayload from 2023.6
Arp.Device.Interface.SdCardStateChanged Info Arp::System::NmPayload::Device::SdCardStateChangedPayload from 2019.0 LTS
Arp.Device.Interface.UserPartitionUsage.Changed Info Arp::System::NmPayload::Device::UserPartitionUsagePayload from 2020.6
Arp.Device.Interface.UserPartitionUsage.Critical Warning Arp::System::NmPayload::Device::UserPartitionUsagePayload from 2020.6
Device UPS
Arp.Device.Ups.UpsHealthFailure
Important: If the system variable UPS_DIAGNOSTICS.HFAIL is TRUE then the controller must be sent to Phoenix Contact for repair. This applies to the controllers AXC F 3152RFC 4072S and BPC 9102S. Please contact Phoenix Contact or your local subsidiary for further details.
Error Arp::System::Nm::StringPayload from 2022.6
Arp.Device.Ups.UpsHealthWarning Warning Arp::System::Nm::StringPayload from 2022.6
Arp.Device.Ups.UpsStateOfChargeGood Info Arp::System::Nm::StringPayload from 2023.6
Arp.Device.Ups.UpsStateOfChargeLow Warning Arp::System::Nm::StringPayload from 2023.6
eCLR
Arp.Plc.Eclr.DcgFailed
(from 2023.6 see Arp.Plc.Domain.DownloadChanges.Failed or  Arp.Plc.Domain.DownloadChanges.Refused)
Error Arp::System::Nm::StringPayload 2022.6 to 2023.3
ESM
Arp.Plc.Esm.Configuration.Validation.Warning Warning Arp::System::Nm::StringPayload from 2024.0 LTS
Arp.Plc.Esm.Exception.Arp.Plc.Esm Error Arp::System::NmPayload::Plc::ExceptionInformationPayload 2019.0 LTS to 2023.9
Arp.Plc.Esm.Exception Error Arp::System::NmPayload::Plc::ExceptionInformationPayload from 2024.0 LTS
GDS
Arp.Plc.Gds.Exception
(from 2023.6 see Arp.Plc.Domain.DownloadChanges.Failed or  Arp.Plc.Domain.Plc.Failed)
Error Arp::System::NmPayload::Plc::Gds::ExceptionInformationPayload 2021.0 LTS to 2023.3
Arp.Plc.Gds.ForceManager.ModeChanged Info Arp::System::NmPayload::Plc::ForceInformationPayload from 2019.9
Arp.Plc.Meta.InvalidProject.PointerInStruct
Error Arp::System::Nm::StringPayload 2021.0 LTS to 2023.3
Arp.Plc.Meta.InvalidProject.PointerToHidden
Error Arp::System::Nm::StringPayload 2020.3 to 2023.3
Interbus
Note: INTERBUS notifications for diagnostics are only registered if an INTERBUS hardware module is present.
Arp.Io.Interbus.Configuration.Error Error Arp::System::NmPayload::Io::Interbus::ServiceErrorPayload from 2023.6
Arp.Io.Interbus.Parameterization.Error Error Arp::System::NmPayload::Io::Interbus::PcpErrorPayload from 2023.6
Arp.Io.Interbus.Error Error Arp::System::NmPayload::Io::Interbus::StatePayload from 2023.6
Modbus Client
Arp.Io.ModbusClient.Error Error Arp::System::NmPayload::Io::ModbusClient::ModbusDiagPayload from 2024.6
Arp.Io.ModbusClient.Info Info Arp::System::NmPayload::Io::ModbusClient::ModbusDiagPayload from 2024.6
Arp.Io.ModbusClient.Warning Warning Arp::System::NmPayload::Io::ModbusClient::ModbusDiagPayload from 2024.6
NotificationLogger
Note: The name for "notification logger archive closed" has become inconsistent. The name up to firmware 2022.0 LTS is really Arp.Service, not Arp.Services. From 2022.6 on, all the notifications from SenderName NotificationLogger start with Arp.Services.
Arp.Services.NotificationLogger.Archive.FileFormatMigrationDowngrade Warning Arp::System::NmPayload::NotificationLogger::StorageFileFormatMigrationPayload from 2022.0 LTS
Arp.Services.NotificationLogger.Archive.FileFormatMigrationFailed Error Arp::System::NmPayload::NotificationLogger::StorageFileFormatMigrationPayload from 2022.0 LTS
Arp.Services.NotificationLogger.Archive.FileFormatMigrationNotPossible Error Arp::System::NmPayload::NotificationLogger::StorageFileFormatMigrationPayload from 2022.0 LTS
Arp.Services.NotificationLogger.Archive.FileFormatMigrationSuccessful Info Arp::System::NmPayload::NotificationLogger::StorageFileFormatMigrationPayload from 2022.0 LTS
Arp.Services.NotificationLogger.Archive.FileIntegrityCheckFailed Error Arp::System::NmPayload::NotificationLogger::StorageFileIntegrityCheckPayload from 2022.0 LTS
Arp.Services.NotificationLogger.Archive.InvalidStorageFile Error Arp::System::NmPayload::NotificationLogger::InvalidStorageFilePayload from 2022.6
Arp.Service.NotificationLogger.ClosingArchive Info Arp::System::NmPayload::NotificationLogger::MessageWithArchiveNamePayload from 2019.0 LTS
Arp.Services.NotificationLogger.ClosingArchive Info Arp::System::NmPayload::NotificationLogger::MessageWithArchiveNamePayload from 2022.6
Notification Manager
Arp.System.Nm.ExceptionDuringNotify.ExternalIoProcess Error Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.System.Nm.ExceptionDuringNotify.LocalIoProcess Error Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.System.Nm.ExceptionDuringNotify.MainProcess Error Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.System.Nm.SubscribeToNotRegisteredNotification Warning Arp::System::Nm::NmSubscribeFailedPayload<Arp::System::Nm::NmSubscribeToNotRegisteredPayload> from 2019.0 LTS
Arp.System.Nm.SubscribeToUnregisteredNotification Error Arp::System::Nm::NmSubscribeFailedPayload<Arp::System::Nm::NmSubscribeToUnregisteredPayload> from 2019.0 LTS
OPC UA® Server
Arp.Services.OpcUAServer (from 2023.3 see Arp.Services.OpcUAServer.StartFailed) Error Arp::System::Nm::StringPayload only 2023.0 LTS
Arp.Services.OpcUAServer.MethodCall  Error Arp::System::Nm::StringPayload from 2020.3
Arp.Services.OpcUAServer.PubSub.Error Error Arp::System::Nm::StringPayload from 2022.6
Arp.Services.OpcUAServer.PubSub.Warning Warning Arp::System::Nm::StringPayload from 2022.6
Arp.Services.OpcUAServer.StartFailed Error Arp::System::Nm::StringPayload from 2023.3
OPC UA® Client
Arp.Services.Modules.OpcUAServer.Client.CloseInternalSessionFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.CreateInternalSessionFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.CreateRemoteSubscriptionFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.GetRemoteSessionFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.LicenseCheckFailed Warning Arp::System::Nm::StringPayload from 2023.0 LTS
Arp.Services.Modules.OpcUAServer.Client.LicenseCheckPassed Info Arp::System::Nm::StringPayload from 2023.0 LTS
Arp.Services.Modules.OpcUAServer.Client.LicenseTrialStarted Info Arp::System::Nm::StringPayload from 2023.0 LTS
Arp.Services.Modules.OpcUAServer.Client.LicenseTrialStopped Warning Arp::System::Nm::StringPayload from 2023.0 LTS
Arp.Services.Modules.OpcUAServer.Client.LocalCreateMonitoredItemFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OPCUAServer.Client.NodeMapping Warning Arp::System::Nm::StringPayload from 2023.6
Arp.Services.Modules.OpcUAServer.Client.OpenInternalSessionFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OPCUAServer.Client.ParseLocalVariable Warning Arp::System::Nm::StringPayload from 2023.6
Arp.Services.Modules.OPCUAServer.Client.ParseRemoteVariableDescriptor Warning Arp::System::Nm::StringPayload from 2023.6
Arp.Services.Modules.OpcUAServer.Client.RemoteCreateMonitoredItemFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.RemoteCreateMonitoredItemsFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.WriteValueToLocalFailed Error Arp::System::Nm::StringPayload from 2023.3
Arp.Services.Modules.OpcUAServer.Client.WriteValueToRemoteFailed Error Arp::System::Nm::StringPayload from 2023.3
PLC Condition Manager
Arp.Plc.Domain.PlcConditionManager.ConditionFailed Info Arp::System::NmPayload::Plc::PlcConditionFailedPayload 2022.0 LTS only
PLC Manager
(2021.0 LTS to 2023.3 see Arp.Plc.Gds.Exception)
Error Arp::System::Nm::StringPayload from 2023.6
Arp.Plc.Domain.DownloadChanges.Refused Warning Arp::System::Nm::StringPayload from 2023.6
Arp.Plc.Domain.Plc.Condition.Failed
(2022.6 to 2023.3 see Arp.Plc.Domain.PlcManager.ConditionFailed)
Arp.Plc.Domain.Plc.Condition.StartingDelayed
(2022.6 to 2023.3 see Arp.Plc.Domain.PlcManager.StartingDelayed)
Error Arp:.System::Nm::StringPayload from 2023.6
Arp.Plc.Domain.Plc.StateChanged
(2019.0 LTS to 2023.3 see Arp.Plc.Domain.PlcManager.StateChanged)
Info Arp::System::NmPayload::Plc::PlcStateChangedPayload from 2023.6
Arp.Plc.Domain.PlcManager.ConditionFailed Info Arp::System::Nm::StringPayload 2022.6 to 2023.3
Arp.Plc.Domain.PlcManager.StartingDelayed Info Arp::System::Nm::StringPayload 2022.6 to 2023.3
Arp.Plc.Domain.PlcManager.StateChanged Info Arp::System::NmPayload::Plc::PlcStateChangedPayload 2019.0 LTS to 2023.3
PLM
Arp.Plc.Plm.DcgNotPossible
(from 2023.6 see Arp.Plc.Domain.DownloadChanges.Refused)
Info Arp::System::Nm::StringPayload 2019.3 to 2023.3
ProfiCloud V3
Arp.Services.ProfiCloudV3.BufferSizeInvalid Warning Arp::System::Nm::StringPayload from 2023.0 LTS
PROFINET Controller
Arp.Io.PnC.Alarm Info Arp::System::NmPayload::Io::ProfinetStack::AlarmPayload2 from 2021.0 LTS
Arp.Io.PnC.ArAbort Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
Arp.Io.PnC.ArReady Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
Arp.Io.PnC.ConfigurationWarning Warning Arp::System::Nm::StringPayload from 2020.6 [1]
Arp.Io.PnC.DcpSignal Internal Arp::System::NmPayload::Io::ProfinetStack::DcpSignalPayload from 2020.3
Arp.Io.PnC.DiagStateChanged Info Arp::System::Nm::StringPayload from 2022.0 LTS
Arp.Io.PnC.PnStationStateChanged Default Arp::System::NmPayload::Io::ProfinetStack::PnStationStatePayload from 2019.0 LTS
Arp.Io.PnC.ResetToFactoryDefaults Info Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.Io.PnC.SetInterfaceAddress Info Arp::System::NmPayload::Io::ProfinetStack::InterfaceAddressPayload from 2019.0 LTS
Arp.Io.PnC.SetStationName Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
  1. only if project was made with PLCnext Engineer 2020.3
PROFINET Device
Arp.Io.PnD.ArAbort Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
Arp.Io.PnD.ArReady Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
Arp.Io.PnD.DcpSignal Internal Arp::System::NmPayload::Io::ProfinetStack::DcpSignalPayload from 2020.3
Arp.Io.PnD.PnStationStateChanged Internal Arp::System::NmPayload::Io::ProfinetStack::PnStationStatePayload from 2019.0 LTS
Arp.Io.PnD.ResetToFactoryDefaults Info Arp::System::Nm::StringPayload from 2019.0 LTS
Arp.Io.PnD.SetInterfaceAddress Info Arp::System::NmPayload::Io::ProfinetStack::InterfaceAddressPayload from 2019.0 LTS
Arp.Io.PnD.SetStationName Info Arp::System::NmPayload::Io::ProfinetStack::MessageWithStationNamePayload from 2019.0 LTS
PROFINET System
Arp.Io.PnS.SystemConfigRestored Warning Arp::System::Nm::StringPayload only 2019.9 and 2020.0 LTS
Redundancy Manager
Arp.Services.RedundancyManager.ErrorOccured Error Arp::System::Nm::StringPayload from 2022.0 LTS
Arp.Services.RedundancyManager.RoleChanged Info Arp::System::NmPayload::Services::Redundancy::RedundancyStateChangedPayload from 2022.0 LTS
Arp.Services.RedundancyManager.StatusChanged Info Arp::System::Nm::StringPayload from 2022.0 LTS
Arp.Services.RedundancyManager.SwitchOver Info Arp::System::Nm::StringPayload from 2022.0 LTS
Arp.Services.RedundancyManager.TypeChanged Info Arp::System::NmPayload::Services::Redundancy::RedundancyStateChangedPayload from 2022.0 LTS
Retain Manager
Note: Up to firmware release 2023.0 LTS the SenderName was PLC Retain.
Arp.Plc.Retain.Error Error Arp::System::Nm::StringPayload from 2020.6
Arp.Plc.Retain.Info Info Arp::System::Nm::StringPayload from 2023.0 LTS
Arp.Plc.Retain.RetainManager Error Arp::System::Nm::StringPayload from 2019.3 to 2020.3
Arp.Plc.Retain.Warning Error Arp::System::Nm::StringPayload from 2020.6
SPLC
Arp.Services.SpnsProxy.General.Notification Info Arp::System::Nm::StringPayload from 2020.3 to 2021.9
Arp.Services.SpnsProxy.General.Notification.Error
(Note: This notifcation will be registered on first use)
Arp.Services.SpnsProxy.General.Notification.Info
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_ACK_REQ Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_CE_CRC Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_CE_CRC_H Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_CHF_ACK_REQ Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_DEVICE_FAULT Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_IPAR_OK Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_LOOPBACK Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_PASS_OUT Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_WD_TIMEOUT Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.F_ADDR_XXXXX_WD_TIMEOUT_H Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Profisafe.ProfisafeCommunicationBit Info Arp::System::NmPayload::Services::SpnsProxy::SpnsProxyProfisafeNotificationPayload from 2020.3
Arp.Services.SpnsProxy.Splc.LedRegisterChanged Internal Arp::System::NmPayload::Services::SpnsProxy::SpnsLedRegisterChangedPayload from 2023.6
Arp.Services.SpnsProxy.Splc.StateChanged Internal Arp::System::NmPayload::Services::SpnsProxy::SpnsStateChangedPayload from 2023.0 LTS
SystemEvents
Arp.Services.SystemEvents.PowerDown Warning Arp::System::Nm::StringPayload from 2022.6
System Manager
Note: This notification is sent with Unregistered state!
Info Arp::System::NmPayload::Acf::SystemStartupPayload from 2019.0 LTS
Arp.System.Acf.SystemManager.StateChanged Info Arp::System::NmPayload::Acf::SystemManagerStatePayload from 2019.0 LTS
System Watchdog
Arp.System.Watchdog.WatchdogStatusChanged Warning Arp::System::NmPayload::SystemWatchdog::SystemWatchdogStateChangedPayload from 2019.9