System redundancy error codes
Available from 2022.0 LTS with RFC 4072R
The most recent status or error message is indicated as a digit, visible in the PLCnext Engineer at the RDNCY_ERROR system variable.
This is how to decode and handle the messages:
Digit
Status or error message
Description
Remedy
1
OwnRdncyTypeChanged
The redundancy type of the controller has been changed.
Restart the controller to apply the modified setting.
2
OwnIPAddressChanged
The IP address has been changed at at least one of the Ethernet interfaces.
3
InvalidIpAddress
At least one IP address is outside of the valid IP address range.
Assign an IP address that is within the valid IP address range to each Ethernet interface that is used.
4
MultipleArpReplies
There are multiple instances of at least one IP address in the connected network.
Make sure that only one instance of each IP address exists.
5
MultiplePeers
No 1-to-1 connection between first and second controller.
Establish a 1-to-1 connection between the first and second controller via the SYNC interface.
6
GetPeerRdncyTypeFailed
Unable to read the redundancy type of the BACKUP controller.
Make sure that there is a 1-to-1 connection between the first and second controller via the SYNC interface.
Restart the BACKUP controller.
7
GetPeerRdncyRoleFailed
Unable to read the redundancy role of the BACKUP controller.
8
RdncyTypeConflict
Both controllers have the same redundancy type.
Assign redundancy type “First” to one of the controllers and redundancy type “Second” to the other controller (see IP settings for redundancy operation). Then restart the respective controller to apply the modified setting.
9
RdncyRoleConflict
Both controllers have the same redundancy role.
The problem is automatically rectified in a few minutes.
10
DifferentPlcTypes
The remote controller is not an RFC 4072R controller.
Replace the remote controller with an RFC 4072R controller.
11
DifferentFirmwareVersions
Different firmware versions are installed on the controllers.
Make sure that the same firmware version is installed on both controllers.
12
SetUserConfigFailed
An error occurred when synchronizing the user roles.
Make sure that there is a 1-to-1 connection between the first and second controller via the SYNC interface. Then restart the BACKUP controller.
13
SetPnNameFailed
During synchronization, an error occurred on the BACKUP controller when setting the PROFINET name.
14
GetIpConfigFailed
An invalid IP address configuration was reported by the BACKUP controller.
If the message occurs again, contact Phoenix Contact.
15
SetIpConfigFailed
During synchronization, an error occurred on the BACKUP controller when setting the IP address configuration.
16
CheckRoleTimeout
Timeout when checking the redundancy roles.
Make sure that the remote controller is fully initialized.
17
ChangeRoleTimeout
Timeout when changing the redundancy roles.
Make sure that the BACKUP controller is fully initialized after it has been restarted.
18
GetInfoTimeout
Data exchange timeout during initialization of the redundant control system.
19
BasicSyncDoneTimeout
Timeout when switching to Basic Sync  redundancy status.
20
TransferApplicationFailed
Error during synchronization: An error occurred when transferring the PLCnext application to the BACKUP controller.
21
StartBackupPlcFailed
An error occurred when starting the BACKUP controller.
22
StopBackupPlcFailed
BACKUP controller: An error occurred when switching to the STOP operating mode.
23
ResetBackupPlcFailed
BACKUP controller: An error occurred when resetting the controller.
127
UnspecifiedError
An unknown error has occurred.
Restart the affected controller.