Alarm function blocks in IEC 61131-3 programming
Introduction
Essential alarm status features
Every alarm is oriented towards the OPC UA Alarms & Conditions specification and has these properties:
Property | Meaning or purpose | Restrictions |
AlarmId |
The unique name of the alarm on the device. | |
AlarmType |
The alarm type can be used for filtering in the client. | |
Active |
The alarm condition is active. | |
Acknowledged |
The user has seen the alarm condition. | |
Confirmed |
The user has solved the problem that caused the alarm. | |
Severity |
The severity of an alarm is set by values from 1 = information to 1000 = severe condition. |
Retain |
The alarm is to be shown to the user (evaluated by the client). | |
Message |
The message to be shown to the user. | |
comment |
The latest comment provided by the user. | firmware 2020.6 or newer |
language |
Identifier of the LocaleID for a comment (according to ISO 639-1 and ISO 3166-1, e.g. "en-US"). | firmware 2020.6 or newer |
user |
The latest user who has acknowledged, confirmed, or changed the comment. | firmware 2020.6 or newer |
Optionally, timestamps
for a variety of substatuses can be set.
Registration of alarms
To introduce an alarm to the system, it has to be registered before the first use. As a result, you can see in the OPC UA® Server which alarms can occur.
Note: It is not possible to remove a registered alarm. However, they are deleted during each cold and warm restart. This is why alarms have to be registered after each cold or warm restart. Registering an alarm twice does not trigger an error message.
Acknowledgement and confirmation of alarms
Some alarms must be acknowledged and sometimes even be confirmed. To do so, the Acknowledge
and Confirm
methods can be used. These are also messages in PLCnext Technology. However, they are sent from a client to the alarm source. The alarm source must process this message. Usually, this results in a new alarm status which, as usual, is sent to all clients.
From firmware 2020.6 and newer, the client can pass a localized comment and the the user's name along with the Acknowledge
and Confirm
properties. This is also reflected in the alarm state.
Additional information to send with the alarm message
Often there is the requirement to add additional information to an alarm, which is available in the client and can be displayed in the message. For this, the alarm state also holds a list of up to 10 custom parameters. These parameters must be entered during registration with their name and data type so that they are known by the client. Elementary data types including strings are supported.
There are alarm blocks that can take on a structure with additional parameters. These parameters must be entered during registration so that they are known to the client. In the message, the parameters can be referenced using placeholders. The following placeholders are supported:
Placeholder | Meaning |
{0} | Alarm name - must be unique within the controller |
{1} | Alarm type |
{2} | 1st user parameter |
{3} | 2nd user parameter |
{11} | 10th user parameter |
The ALM_ALARM
and ALM_ALARM_PARAM
function blocks implement defined semantics of the alarms. Via Requires Acknowledge
and Requires Confirm
, you can only specify if the alarm is to be acknowledged or confirmed.
For more complex scenarios, you can write your own alarm blocks. This way you can, for example, check additional conditions, implement a different time behavior, or implement several alarms with a single block. For these tasks, the ALM_CUSTOM_ALARM
block is available. It provides the low level methods that were used for implementing the other blocks.
Using Alarm function blocks in IEC 61131-3 programming
IEC 61131 alarm function blocks
The alarm function blocks are contained in the PLCnext Controller library.
There are three types of alarm function blocks:
- Standard alarm blocks (
ALM_REGISTER
,ALM_ALARM
) - Blocks with user parameters (
ALM_REGISTER_PARAM
andALM_ALARM_PARAM
) - A support class for user-defined alarm blocks (
ALM_CUSTOM_ALARM
Alarm blocks use theALM_ALARM
structure for internal data storage. It is used by the blocks, and ouside of the blocks this structure shall only be read.
TheALM_REGISTER
alarm block
To register an alarm, you can use the ALM_REGISTER
function block. A rising edge or constant TRUE
signal at the input introduces the alarm to the system. This function block must be called until the DONE
output delivers a TRUE
signal. If many alarms are registered at the same time, aFALSE
signal might occur.
Several alarms can be registered in the same PLC cycle. However, if the DONE
output sends a FALSE
signal, the registration can only be continued during the next cycle.
The ALM_ALARM
alarm block
To send alarm statuses, you can use the ALM_ALARM
function block. With each change of the ACTIVE
input, the new status is sent to the OPC UA server. This function block must be called until the DONE
output issues a TRUE
signal. If many alarms are transmitted at the same time, a FALSE
signal might occur. In this case, the call must be tried again in the next cycle.
The AUTO_ACK
and AUTO_CONF
inputs can be used to control if alarms require acknowledgement or confirmation. If both inputs are set to TRUE
, the alarm will disappear as soon as the condition at the ACTIVE
input changes to FALSE
again.
If acknowledgement or confirmation is desired, the function block has to process these requirements. It is therefore required that the function block is called continuously so that it can internally process these messages.
To send user-defined parameters together with an alarm, you can use extended function blocks:
The user-defined parameters have to be introduced to the server via a structure. You can define and use a structure of up to ten parameters. The parameters must each have an elementary data type including strings. ForALM_REGISTER_PARAM
, the names and types of the structure components are taken from the data type definition (worksheet) as names and types for the parameters.
For theALM_ALARM_PARAM
function block, the values from the structure are transmitted with the alarm status.
User-defined alarm blocks
Use theALM_CUSTOM_ALARM
function block to create your own alarm blocks. This might be useful if special timing or a specific filter is required, for example. In addition, you can use the user-defined alarm block to set another semantics ofACK
,CONF
orRETAIN
or implement several alarms in a combined function block.
TheALM_CUSTOM_ALARM
function block provides access to methods of the subordinate alarm system. All methods are implemented as methods of the block.
The following methods send the corresponding messages to the OPC UA server:
SendAcknowledge
SendAddAlarm
SendConfirm
SendStateChange
Use the GetAckConfRequest
method to handle Acknowledge
, Confirm
or AddComment
calls of the client.
Acknowledging and confirming alarms
Instead of the OPC UA Server, you can also use the ALM_ACK
and ALM_CONF
function blocks to acknowledge and confirm any alarm. The alarms are clearly identified by the ALARM_ID
Related Topics